+rep, thankS so much! I have been looking around online for about three hours and found a wiring diagram for this outlet at PLATT. EXCELLENT website for electrical. It appears that yes, the NEMA 6 gets wired hot, hot, ground. I will cap the neutral and check the outlet with my testers.
My Quantum ballasts say 4.1A at 240V (8A at 120V). I will be using the 240V cords that came with them.
THANK YOU AGAIN!!
I like to leave electrical to the daredevils (electricians) but I'd hate to have to kill one after he helped me set up my grow.
OKAY WAIT A SECOND HERE............ I'm an electrician, and I will explain everything you need to know so you will feel confident enough to wire this up properly..
First off why would you want to run your ballast on 240v? The ONLY reason to do this is to minimize the cost of buying wire to feed the room.. it will not have any impact on your electricity bill at all.. 120v x 8 amps = 960watts.... and guess what? 240v x 4 amps gives you.... tada! 960watts... exactly the same wattage.. and you are billed on your total watts used.. therefore you see why it has no impact on your electricity bill.
If you are tripping your breaker by plugging in a ballast then the circuit is obviously being shared with other appliances, a 15A breaker can cold 12A steady.. 80% of capacity.. switching the ballast to 240 will not work in this situation because every thing in your house runs off 120V, if you were to switch the wires at the panel you would be giving 240V to everything on that circuit.. so the other items that were causing the breaker to trip would be getting way too much voltage and burn out..
If you have more then one ballast (three 1000w ballasts) running in the grow room then and ONLY then it would be smart to switch to 240V.. Why? I will explain... This will be a little long winded I can imagine.. just hit a bowl of super lemon haze... yum yum...
running one 1000w ballast in one room (120V)
- need one 15 amp circuit at panel
- need one 14/2 wire running to the room
- put the wire into a box, add a plug and plug in your light..
Total watts 960w.. like stated above.
Running two ballast in one room..
- need EITHER 1 x 14/3 wire from 1 2-pole 15 amp breaker in panel to the room, where it goes into a box and the box has two receptacles one for each ballast to plug into.
- OR YOU CAN RUN 2 x 14/2 wires from two 15 breakers in your panel to the room and each wire goes into two a box with a receptacle and a ballast plugs into each one...
2ballasts x 8A (each light draws) x 120 v = 1920 W.... double the amount as one ballast..
Running three ballasts at 120
- need three 15A breakers in the panel, with three separate runs going to each box with receptacle, and each light plugs into it.. Just like the two previous situations
- total is 960W x 3 = 2880W....
Running three ballasts at 240V
- need 1 x 14/3 from 1 x 2-pole 15A breaker to the room.. this time the wires going into a box or ganged boxes with three 240V plugs in it... or easier three "dpdt" switches, which are double pole double throw.. allows two conductors to be switched at the same time with one switch.. used for 240V all the time because you need to shut off both of the conductors to the item not just one like in the 120V situation we are used to.
- so 3 x 4A x 240V = 2880W EXACTLY THE SAME AS IF YOU WERE TO RUN THREE CIRCUITS TO THE ROOM AND HAVE EACH LIGHT AT 120V......
So why would you run lights at 240V in the first place? Look at how much money is spent on material to set up each of these situations...... or more specifically the three ballast situations.. it is much more expensive (depending on distance from the panel to the room) to get three runs of 14/2 wire plus three breakers/boxes/plugs.... then it is to run one 14/3 wire, one 15A 2-Pole breaker and the boxes and three dpdt switches..
So that is it.... there is no real reason to run your ballasts on 240V if you are not running three or more ballasts.. yes there are more details to this, but that is as basic as I can put it.. the out of pocket expense to install the system is the only monetary ($$$$$) benefit you will ever see from it.
If you have Q's please fire away.. time for another bowl....