ASMALLVOICE
Well-Known Member
Too Kewl. Many thanx for the reply.The PH dosing pumps have the same manual control Screen. This is because at any given time an operator should be able to control a pump manually to inspect its function. Beyond this, yes, the PH is controlled up and down via a PID function, and automatically adjusted. The accuracy of the automatic dosing is essentially a function of the deadband, which is also set by the user. If you'd like to hold a PH of 5.8, and you set the dead band to .2 ph, your PH will be allowed to swing between 5.6 and 6.0 ph, or .2 ph on either side of the setpoint. However, if you set the deadband to .1 ph, now the controller will automatically control the PH to a value between 5.7 and 5.9 for a setpoint of 5.8.
The goal of the controller at this point is to be cable of maintaining a .05 ph deadband, or a range of 5.75 to 5.85 for a setpoint of 5.8.
The testing phase of the controller will really prove out the capabilities.
Looking forward to seeing it in action.
Peace and Great Grows
Asmallvoice