TurboTokes
Well-Known Member
A sparky will run a new circuit from a breaker panel to a room in the house for $200ish
about how much would it run?Find an electrician doing side jobs.
SPARKY?A sparky will run a new circuit from a breaker panel to a room in the house for $200ish
An electrician . Most guys working after hours charge about half of what a company would. I'm guessing less than $200-$300 and worth it. Safety has no price limit.SPARKY?
true true, my house has 200 amp service you think a 20 amp would run 7000w? 5 1000w lights and all the bells and whisltesAn electrician . Most guys working after hours charge about half of what a company would. I'm guessing less than $200-$300 and worth it. Safety has no price limit.
That I am not qualified to answer.true true, my house has 200 amp service you think a 20 amp would run 7000w? 5 1000w lights and all the bells and whisltes
okay thanks!That I am not qualified to answer.
The ballast will not fail, the capacitors fail.in them reducing output and you will never notice it at all other then reduced production, I personally would only use a electronic ballast , they are consistent in output and run a lot cooler,I have never (yet) had a magnetic ballast just fail. Heavy but also no RFI/EMI problems.
BUT 5 1000W BALLAST IN A RESIDENTAL NEIGHBOR HOOD IN CALI?The ballast will not fail, the capacitors fail.in them reducing output and you will never notice it at all other then reduced production, I personally would only use a electronic ballast , they are consistent in output and run a lot cooler,
Just my two cents ,
No. You want a double 30 amp on a 10 gauge wire running on 240v just for the lights. That will run 5 1k's but no more safely since will be close to 80% load on the 30 amp.true true, my house has 200 amp service you think a 20 amp would run 7000w? 5 1000w lights and all the bells and whisltes
7000 watts would take around 35 amps to run at 220 volts , you would need and want a 50 amp 220 volt breaker in the panel for it , that will give you some over current protection you will need another two 20 amp 110 volt circuits and 2.5 tons of cooling to three tons of cooling ( 30k to 36 k btu) to cover the cooling of the bulbs and any other loads, the amps for that will be around 40 amps for the cooling unit unless you go with the mini split system then it will be around 15 amps if I remember correctly ,true true, my house has 200 amp service you think a 20 amp would run 7000w? 5 1000w lights and all the bells and whisltes
5k watts of lights air cooled, planning on no cooling system as they will be air cooled reflectors venting outside7000 watts would take around 35 amps to run at 220 volts , you would need and want a 50 amp 220 volt breaker in the panel for it , that will give you some over current protection you will need another two 20 amp 110 volt circuits and 2.5 tons of cooling to three tons of cooling ( 30k to 36 k btu) to cover the cooling of the bulbs and any other loads, the amps for that will be around 40 amps for the cooling unit unless you go with the mini split system then it will be around 15 amps if I remember correctly ,
Each 1000 wat balast pulls around 5 amps each at 220 volt, for seven bulbs will be 35 amps by itself , I do not remember the exact amps but it was around 5 amps per thousand fixture , then you want the wire over sized for future use of the circuit also and a little for over current protection of the circuit ,No. You want a double 30 amp on a 10 gauge wire running on 240v just for the lights. That will run 5 1k's but no more safely since will be close to 80% load on the 30 amp.
If you go this route you will have to make sure you design the duct work for the hood system or ventilation of the room correctly or it will not work , especially with the heat of 7000 watts of bulbs5k watts of lights air cooled, planning on no cooling system as they will be air cooled reflectors venting outside
Only (5) 1k watt bulbs, the 7k was the whole grow, timers, fans, and ballast and everything. The ducting would be insulated and go strictly in then thru the hoods then exhaust out, no gaps, or open air and an 800cmf fan to be sure the bulbs stay coolIf you go this route you will have to make sure you design the duct work for the hood system or ventilation of the room correctly or it will not work , especially with the heat of 7000 watts of bulbs
Not even close. Even three 20 amp circuits would be maxed out. 7000 watts is nearly 60 amps at 120 volts or about 30 amps at 240. 4-20 amp circuits is what you need to run safely and reliably.true true, my house has 200 amp service you think a 20 amp would run 7000w? 5 1000w lights and all the bells and whisltes
So then I should get two 30amp 240v lines run to the room? When you say 240v can I still run regular cords to that? The ones that just run regularly into the wall? Or do I need like special plugs for each lightNot even close. Even three 20 amp circuits would be maxed out. 700 watts is nearly 60 amps ay 120 volts or about 30 amps at 240. 4-20 amp circuits is what you need to run safely and reliably.
Yeah, that's exactly the type of guy you want to let into your house where you will be growing cannabis.Find an electrician doing side jobs.